Running 3 phase 780s on single phase power (was RE: hams on classiccmp)
Patrick Finnegan
pat at computer-refuge.org
Mon Jan 19 13:59:53 CST 2009
On Monday 19 January 2009, Roger Holmes wrote:
> > But, if you run the same load from three separate single phase
> > circuits
> > and (worst case) the three circuits are all the same phase, then
> > the neutral
> > current will be the SUM of all three phase currents. That's 3
> > times what it
> > would be otherwise and runs a serious danger of melting the neutral
> > and
> > starting a fire.
>
> I agree with all but the last bit, because if he's running it from
> three separate supplies, surely he will have three neutral
> conductors, so no problem.
Not if he uses the original pdu and original power cord, which has only
a single 10AWG neutral conductor.
Pat
--
Purdue University Research Computing --- http://www.rcac.purdue.edu/
The Computer Refuge --- http://computer-refuge.org